I spent over 20 years in the electricity supply industry and have seen several hundred installations in my time. Regulations change as we know and I've often found wiring to different editions within the same overall installation. I frequently found 'extended' circuits that do not meet reg's for one reason or another. The most important point for me is that an installation is safe; polarity, earthing and appropriate fusing, meeting current (preferably) or appropriate reg's for the time. It may be possible for you to 'fuse down' part of your installation at the consumer unit to ensure you do not overload the circuit with too much load (too many appliances) for the cable to carry. Ring main circuits are typically fused at 30 amps which is more current than one 2.5mm t&e supply cable (spur) is designed to carry. There is a part of my own installation (to a building extension, as inhereted by me) that should have been wired as an extension to one of the existing rings but had been wired as several spurs. The only practical solution to this particular issue, without major decorative disruption was to fuse down the whole circuit, in this case fitting a 16amp MCB to the distribution board (which is backed by a RCD of course for this type of circuit). It is extremely unlikely that the demands of my circuit will ever exceed 16 amp unless several heating appliances are connected at the same time. You may be able to do this for your circuit depending on the way your installation is wired and the load that that part of the installation is required to carry. You could otherwise (if practical) fit a fusing point at the point the spur is connected to the ring main effectively fusing down that part of the installation.