One for those with electrical knowledge
« on: 23 September 2012, 21:12:02 »

Evenin' all, can anyone tell me if it is o.k. to run the pump on a gas boiler of the upstairs lighting circuit? The reason I ask is my daughter has just had a boiler fitted in the loft and the installers have tapped into the lighting circuit to feed the pump, I would have thought that this wouldn't be "best practice" but I could be wrong.
TIA
Tony
Logged
Be aware of mole holes be very aware!

Marie

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Female
  • Linconshire but works in oxfordshire
  • Posts: 2676
  • i am a hands on person, i like to get stuck in !!!
    • 2ltr LPG Estate
    • View Profile
Re: One for those with electrical knowledge
« Reply #1 on: 23 September 2012, 21:25:23 »

I couldnt tell you personally but my dad is a plumberand heating engineer, cant call him tonight as its now a bit late but i can tomorrow for you if youd like
Logged
Now has two miggs in our house hold. Both 2.0ltr 16v lpg'd. a MFL and a FL.

jonny2112

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Bangor NI
  • Posts: 3047
    • 2.6 Elite
    • View Profile
Re: One for those with electrical knowledge
« Reply #2 on: 23 September 2012, 21:30:56 »

Lighting circuits are lighter than normal mains, and whilst I have no real knowledge, I would have thought it should have been off the mains  :-\
Lighting is 1.5mm whilst the mains is heavier at 2.5mm.
I guess it will depend on the boiler requirements.
Logged

TheBoy

  • Administrator
  • *****
  • Offline Offline
  • Gender: Male
  • Brackley, Northants
  • Posts: 107031
  • I Like Lockdown
    • Whatever Starts
    • View Profile
Re: One for those with electrical knowledge
« Reply #3 on: 23 September 2012, 21:32:55 »

I thought all parts of the central heating should be off a dedicated circuit  :-\
Logged
Grumpy old man

Tony H

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • liverpool
  • Posts: 4940
  • Black Elites are luurvley
    • View Profile
Re: One for those with electrical knowledge
« Reply #4 on: 23 September 2012, 21:33:59 »

I couldnt tell you personally but my dad is a plumberand heating engineer, cant call him tonight as its now a bit late but i can tomorrow for you if youd like
Thanks for that Marie I would appreciate it  :y.

Logged
Be aware of mole holes be very aware!

jonny2112

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Bangor NI
  • Posts: 3047
    • 2.6 Elite
    • View Profile
Re: One for those with electrical knowledge
« Reply #5 on: 23 September 2012, 21:35:50 »

I thought all parts of the central heating should be off a dedicated circuit  :-\

Yes, I would have thought a boiler should definitely have its own circuit.
Logged

Marie

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Female
  • Linconshire but works in oxfordshire
  • Posts: 2676
  • i am a hands on person, i like to get stuck in !!!
    • 2ltr LPG Estate
    • View Profile
Re: One for those with electrical knowledge
« Reply #6 on: 23 September 2012, 21:45:32 »

I couldnt tell you personally but my dad is a plumberand heating engineer, cant call him tonight as its now a bit late but i can tomorrow for you if youd like
Thanks for that Marie I would appreciate it  :y.

noworries Tony could you post the make and model of the boiler for me and the pump if you can get it and ill ring dad at lunch tomorrow andlet you know.
Logged
Now has two miggs in our house hold. Both 2.0ltr 16v lpg'd. a MFL and a FL.

Martian

  • Guest
Re: One for those with electrical knowledge
« Reply #7 on: 23 September 2012, 21:49:11 »

No it's not alright.

A switched FCU should be fed using a minimum 2.5mm˛ cable as it is capable of being fitted with a 13A fuse.
The feed to the boiler should have been taken from an RCD protected ring main, or from it's own dedicated MCB/RCBO in the CU.
The person fitting it also needs to be Part P certified.
Logged

Andy B

  • Get A Life!!
  • *****
  • Offline Offline
  • Gender: Male
  • Bury Lancs
  • Posts: 39778
    • ML350 TDM SmartRoadster
    • View Profile
Re: One for those with electrical knowledge
« Reply #8 on: 23 September 2012, 21:52:54 »

....
The person fitting it also needs to be Part P certified.

hence self contained boilers having a plug on them ........ therefore no need for the cert.  :y :y :y
Logged

Kevin Wood

  • Global Moderator
  • *****
  • Offline Offline
  • Gender: Male
  • Alton, Hampshire
  • Posts: 36417
    • Jaguar XE 25t, Westfield
    • View Profile
Re: One for those with electrical knowledge
« Reply #9 on: 23 September 2012, 21:53:16 »

.. and the pump should, more often than not, be fed from the boiler as a lot of modern boilers have a pump overrun feature that keeps the pump running until the boiler has cooled off after firing.
Logged
Tech2 services currently available. See TheBoy's price list: http://theboy.omegaowners.com/

Martian

  • Guest
Re: One for those with electrical knowledge
« Reply #10 on: 23 September 2012, 22:08:19 »

....
The person fitting it also needs to be Part P certified.

hence self contained boilers having a plug on them ........ therefore no need for the cert.  :y :y :y
Still need to sign off when you fit either the socket or FCU that is supplying it though (if it's not there already as in the OP's case)  ;)
Logged

Andy B

  • Get A Life!!
  • *****
  • Offline Offline
  • Gender: Male
  • Bury Lancs
  • Posts: 39778
    • ML350 TDM SmartRoadster
    • View Profile
Re: One for those with electrical knowledge
« Reply #11 on: 23 September 2012, 22:13:42 »

....
The person fitting it also needs to be Part P certified.

hence self contained boilers having a plug on them ........ therefore no need for the cert.  :y :y :y
Still need to sign off when you fit either the socket or FCU that is supplying it though (if it's not there already as in the OP's case)  ;)
:y :y :y
Which goes to show that there must be loads of houses that wouldn't pass muster ........  ;D ;D ;D
Logged

Rods2

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Sandhurst Berkshire
  • Posts: 7604
    • 1999 3.0 Elite Estate
    • View Profile
Re: One for those with electrical knowledge
« Reply #12 on: 24 September 2012, 02:36:11 »

Yeeh har! What was the companies name Tonto and the Lone Ranger Plumbers Ltd. 1, Cowboy Trail, Texas :o :o :o :o

Are they Gas registered and do they have part P. I suspect not for the latter, what about the former? No it is a big no, no, to take the boiler or pump feed off a lighting circuit.

Sounds like they have cut more corners than The Sweeney in a high speed car chase.  :D :D :D

Yeeh har!
Logged
US Fracking and Saudi Arabia defending its market share = The good news of an oil glut, lower and lower prices for us and squeaky bum time for Putin!

tigers_gonads

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Kinston Upon Hull
  • Posts: 8610
  • Driving a Honda CR-V which doesn't smell of pee
    • Honda CR-V
    • View Profile
Re: One for those with electrical knowledge
« Reply #13 on: 24 September 2012, 08:56:57 »

As Martian says  :y

Your boiler should be run from a seperate circuit on your consumer unit.
If its just a standard domestic combi boiler, you can run the cable in 1.5mm T&E with a 6 amp breaker at the consumer unit end and a 3 amp fuse fitted into the switched fuse spur.
The circuit must be rcd protected.

It "should" be signed off by a part p sparky  :y
Logged

Elite Pete

  • Omega Queen
  • *****
  • Offline Offline
  • Gender: Male
  • Chester
  • Posts: 19580
  • My spider senses are tingling
    • Audi SQ5 GSX1400
    • View Profile
Re: One for those with electrical knowledge
« Reply #14 on: 24 September 2012, 09:03:11 »

I take it your daughter doesn't live in Liverpool then Tony or the boiler would have been wired into next doors :P ;D ;D
Logged