Moving on from TH's central heating problem.....
« on: 17 December 2011, 15:13:30 »

My Central heating is about 30yrs old......8 rads, all connected using microbore pipework.
Boiler is 30yrs old too  :o and i plan to change it next year....

However I think it may need a descaling/desludging, since ive added a digital room stat......ive noticed on cold nights, that the stat is still calling for heat even after the heating has been on after 4hours (stat set on 20c) Ive had double glazing this year and the house has cavity wall insulation with about a foot of loft insulation.......so it carnt be losing that much heat!

All the rads get hot (upstairs not as hot as downstairs)  and all the rads still keep getting hotter even after the heating has been on for hours.

I know the boiler is old.....but I think maybe the water isnt circulating as it should.

Ive turned off the bypass valve (rad in bathroom doesnt have a stat on it and is left fully on all the time) which helped the rads upstairs get hotter.

Pump is set on 2, i could turn it up to 3, but i think that will just put more strain on it.

So my question is, looking at the fernox website, there are quite different products available.
Is it better to tip the descaller  in the header tank or use one of those aerosol type ones direct into a rad?

I noted that Millwall (in TH's thread) left the descaller in for 2 weeks before flushing it.....is this amount of time it should be left in for, for it to work?  :-\

Ta muchly....
Logged

Taxi_Driver

  • Guest
Logged

paul.lovejoy

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Ramsgate Kent
  • Posts: 2691
    • wife mad 2.6 cd estate
    • View Profile
Logged

Kevin Wood

  • Global Moderator
  • *****
  • Offline Offline
  • Gender: Male
  • Alton, Hampshire
  • Posts: 36384
    • Jaguar XE 25t, Westfield
    • View Profile
Re: Moving on from TH's central heating problem.....
« Reply #3 on: 17 December 2011, 17:05:02 »

I would check the basics first. Has it been properly balanced? Get a couple of clip-on thermometers, get it all working and open any TRVs so all radiators are flowing and then measure the temperature drop across each radiator. Adjust the flow valves to get about 10 degrees C drop across each radiator. If you can't achieve this you have too little flow through the system.

I would have thought a microbore system would need the pump on maximum speed - if you can put up with the noise, but the temperature drop is key to whether it's flow rate that's the problem.

Failing the above, is the boiler thermostat set high enough?

I'm not sure how effective an additive will be. If a boiler change is on the cards, might be worth waiting for now, and getting it powerflushed when that time comes.
Logged
Tech2 services currently available. See TheBoy's price list: http://theboy.omegaowners.com/

millwall

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • se london
  • Posts: 3138
  • no muff too tuff
    • accord type s
    • View Profile
Re: Moving on from TH's central heating problem.....
« Reply #4 on: 17 December 2011, 17:07:11 »

My Central heating is about 30yrs old......8 rads, all connected using microbore pipework.
Boiler is 30yrs old too  :o and i plan to change it next year....

However I think it may need a descaling/desludging, since ive added a digital room stat......ive noticed on cold nights, that the stat is still calling for heat even after the heating has been on after 4hours (stat set on 20c) Ive had double glazing this year and the house has cavity wall insulation with about a foot of loft insulation.......so it carnt be losing that much heat!

All the rads get hot (upstairs not as hot as downstairs)  and all the rads still keep getting hotter even after the heating has been on for hours.

I know the boiler is old.....but I think maybe the water isnt circulating as it should.

Ive turned off the bypass valve (rad in bathroom doesnt have a stat on it and is left fully on all the time) which helped the rads upstairs get hotter.

Pump is set on 2, i could turn it up to 3, but i think that will just put more strain on it.

So my question is, looking at the fernox website, there are quite different products available.
Is it better to tip the descaller  in the header tank or use one of those aerosol type ones direct into a rad?

I noted that Millwall (in TH's thread) left the descaller in for 2 weeks before flushing it.....is this amount of time it should be left in for, for it to work?  :-\

Ta muchly....

i use X800 Jetflo Ultimate Cleaner  but i also powerflush  which combined gives excellent results :y
Logged

Taxi_Driver

  • Guest
Re: Moving on from TH's central heating problem.....
« Reply #5 on: 17 December 2011, 20:36:13 »

I would check the basics first. Has it been properly balanced? Get a couple of clip-on thermometers, get it all working and open any TRVs so all radiators are flowing and then measure the temperature drop across each radiator. Adjust the flow valves to get about 10 degrees C drop across each radiator. If you can't achieve this you have too little flow through the system.

I would have thought a microbore system would need the pump on maximum speed - if you can put up with the noise, but the temperature drop is key to whether it's flow rate that's the problem.

Failing the above, is the boiler thermostat set high enough?

I'm not sure how effective an additive will be. If a boiler change is on the cards, might be worth waiting for now, and getting it powerflushed when that time comes.

Didnt knpw you had to balance each rad  ::)

As said its a 30yo system and afaik its only had a weak attempt to flush it about 5 years ago when the rads upstairs stopped working......then i used an aerosol type flusher and inhibitor injected into a bleed valve of a rad, but i only left the flusher in for about a day, coz the rads upstairs started working again. Other than that its been untouched i think.

Boiler stat is set on 4 out of 6 max
« Last Edit: 17 December 2011, 20:39:42 by Taxi Driver »
Logged

millwall

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • se london
  • Posts: 3138
  • no muff too tuff
    • accord type s
    • View Profile
Re: Moving on from TH's central heating problem.....
« Reply #6 on: 17 December 2011, 21:33:15 »

taxi have a read here  http://www.shadlock.co.uk/energy/heat/chbal.htm    will give you something to go on  although your system is old so a chemical and powerflush is the route i would go for a start
Logged

Taxi_Driver

  • Guest
Re: Moving on from TH's central heating problem.....
« Reply #7 on: 18 December 2011, 08:19:03 »

taxi have a read here  http://www.shadlock.co.uk/energy/heat/chbal.htm    will give you something to go on  although your system is old so a chemical and powerflush is the route i would go for a start

Thankyou all, interesting read Millwall  :y
Logged

Sir Tigger KC

  • Get A Life!!
  • *****
  • Online Online
  • Gender: Male
  • West Dorset
  • Posts: 24528
    • Ford Mondeo 2.2TDCi TitX
    • View Profile
Re: Moving on from TH's central heating problem.....
« Reply #8 on: 18 December 2011, 11:07:36 »

Is it true though that power flushing might not be the best idea in an old system? As it's too much pressure and can cause leaks?  ???
Logged
RIP Paul 'Luvvie' Lovejoy

Politically homeless ......

paul.lovejoy

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Ramsgate Kent
  • Posts: 2691
    • wife mad 2.6 cd estate
    • View Profile
Re: Moving on from TH's central heating problem.....
« Reply #9 on: 18 December 2011, 11:13:43 »

Is it true though that power flushing might not be the best idea in an old system? As it's too much pressure and can cause leaks?  ???

tell me about it think i am suffering with that this morning :o ;D

hot flush, what am i like :-*
Logged

Sir Tigger KC

  • Get A Life!!
  • *****
  • Online Online
  • Gender: Male
  • West Dorset
  • Posts: 24528
    • Ford Mondeo 2.2TDCi TitX
    • View Profile
Re: Moving on from TH's central heating problem.....
« Reply #10 on: 18 December 2011, 11:21:09 »

At least you're not getting a back flush Paul!!!!  :o :o :o
Logged
RIP Paul 'Luvvie' Lovejoy

Politically homeless ......

Taxi_Driver

  • Guest
Re: Moving on from TH's central heating problem.....
« Reply #11 on: 18 December 2011, 17:32:02 »

I would check the basics first. Has it been properly balanced? Get a couple of clip-on thermometers, get it all working and open any TRVs so all radiators are flowing and then measure the temperature drop across each radiator. Adjust the flow valves to get about 10 degrees C drop across each radiator. If you can't achieve this you have too little flow through the system.

I would have thought a microbore system would need the pump on maximum speed - if you can put up with the noise, but the temperature drop is key to whether it's flow rate that's the problem.

Failing the above, is the boiler thermostat set high enough?

I'm not sure how effective an additive will be. If a boiler change is on the cards, might be worth waiting for now, and getting it powerflushed when that time comes.

Just been reading the guide that Millwall posted a link to.....it doesnt rate the clip on thermometers and recommends using a laser one......so i've just reserved one of these....

http://www.maplin.co.uk/infrared-thermometer-with-laser-targeting-223005  :y
Logged

Taxi_Driver

  • Guest
Re: Moving on from TH's central heating problem.....
« Reply #12 on: 18 December 2011, 17:35:42 »

Is it true though that power flushing might not be the best idea in an old system? As it's too much pressure and can cause leaks?  ???

Not sure...... :-\

However on some of the descalling compounds i've been looking at, its says dont use this product if the system is prone to leaks.....but you can get products to fix any leaks......but i guess its like adding radweld to leaking car radiator......and some will advise not using it  :-\
Logged

Shackeng

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Ramsbury
  • Posts: 7762
    • 3.2 Elite 2.0 TitX Mondeo
    • View Profile
Re: Moving on from TH's central heating problem.....
« Reply #13 on: 18 December 2011, 18:28:56 »

This link may be helpful, if not, register free with DIYnot.com, and post your questions, a plumber will answer it very quickly. I've used this site for years, and find it very useful.
http://www.diynot.com/forums/viewtopic.php?p=1167325#1167325

HTH :y :y :y
Logged

Taxi_Driver

  • Guest
Re: Moving on from TH's central heating problem.....
« Reply #14 on: 18 December 2011, 19:41:34 »

This link may be helpful, if not, register free with DIYnot.com, and post your questions, a plumber will answer it very quickly. I've used this site for years, and find it very useful.
http://www.diynot.com/forums/viewtopic.php?p=1167325#1167325

HTH :y :y :y

Thanks for the link......i've been reading through the pages that Millwall posted a link to.....

So my plan is bung in descaller/sludge remover....

While thats working on the system.......build heat reflectors for 5 of my rads (5 rads are attached to outside walls)

After the descaller has done its job and ive fitted the heat reflectors.......then try to balance the rads.....

Job should be jobbed by then........and it will probably be summer again by then  ;D